Author Topic: Wrong indication of Maximum Temperature in a 2D slice at igniter location  (Read 625 times)

sujee

  • New Member
  • *
  • Posts: 3
    • View Profile

Hello All
  Though I applied a temperature of 10000C for the igniter, the temperature profile extracted for a vertical plane at igniter point shows 420 C as the highest reading. I have also used few thermocouples at igniter point, which shows ~700-8000C. Would any of you help me to figure out the reason behind it?
Thanks.
Logged

jharbold

  • Member
  • **
  • Posts: 26
    • View Profile

Are your meshes small enough to capture this temperature gradient?  Did you perform a mesh sensitivity analysis?
Logged

sujee

  • New Member
  • *
  • Posts: 3
    • View Profile

Thank you so much for you response!
I used 0.5 m element size. I didn't try mesh sensitivity analysis.
Logged

jharbold

  • Member
  • **
  • Posts: 26
    • View Profile

Do some research to try to understand what the proper mesh size should be.  Maybe try 0.1m or 0.05m.  Notice if this fixes your problem.  Create some temperature slice files to understand the temperature flow during the simulation - does this flow represent your expectations?